Since HIT-RE 500 V3 is epoxy, is it better than HY-200 in vibration loading?
Hi Billy,
Please click here to access the guide from the Hilti UK website. Specifically, please review the summary on Page 14,
Section 2.4.6.
Regards,
Ashley
Tom,
Currently in North America there are no standards or qualifications tests for dynamic loading on post-installed anchor systems; however, some Hilti anchors are noted as "may be suitable" for dynamic loading based on European testing (https://submittals.us.hilti.com/PTGVol2/#6). To assist with the design, many customers will reference the HIlti European Dynamic Design guide (https://www.hilti.fi/medias/sys_master/documents/h3a/9107966591006/Dynamic-design-of-anchors-Brochure-ASSET-DOC-LOC-2521843.pdf) in order to make an engineering judgement for the anchor system.
Let us know if you have any additional questions.
Regards,
Bryan