We are installing a lightning proteciton system on a fire station in Cape Coral. We have 2 scenarios where we can either pass the conductor through the 2 hour fire wall and fire caulk it or use a 1/2" threaded rod through the wall and caulk it with a fire caulk. Looking to see if you have a detail approved for this type of applicaiton?
Hi Lance. Thank you for utilizing ASK Hilti! Please utilize the attached tested system W-L-7130 for the application described above.
We can create an engineering judgement to show you how to install a fire rated system, specifically calling out "conductor", by submitting an EJ request form to usfirestopeng@hilti.com if you desire.
Also, you are able to search for all Hilti approved firestop systems, like W-L-7130, by utilizing Hilti firestop system selector. See link below.
Follow link: https://www.hilti.com/content/hilti/W1/US/en/services/fasteners-firestop-strut/firestop-portfolio.html
Thank You for choosing Hilti as your Firestop Experts!
Best Regards,
Raymond Prescott V, Fire Protection Engineering Team