Do you have a detail for a lightning protection conductor going through a 2 hour firewall? Or a 1/2" all-thread pasing through the firewall?

Posted by Lance Flemingalmost 6 years ago
Do you have a detail for a lightning protection conductor going through a 2 hour firewall? Or a 1/2" all-thread pasing through the firewall?

We are installing a lightning proteciton system on a fire station in Cape Coral. We have 2 scenarios where we can either pass the conductor through the 2 hour fire wall and fire caulk it or use a 1/2" threaded rod through the wall and caulk it with a fire caulk. Looking to see if you have a detail approved for this type of applicaiton?

lightning,protection

2 Replies
Posted by Raymondalmost 6 years ago
Hilti Verified

Hi Lance. Thank you for utilizing ASK Hilti! Please utilize the attached tested system W-L-7130 for the application described above.

We can create an engineering judgement to show you how to install a fire rated system, specifically calling out "conductor", by submitting an EJ request form to usfirestopeng@hilti.com if you desire.

Also, you are able to search for all Hilti approved firestop systems, like W-L-7130, by utilizing Hilti firestop system selector. See link below.

Follow link: https://www.hilti.com/content/hilti/W1/US/en/services/fasteners-firestop-strut/firestop-portfolio.html

Thank You for choosing Hilti as your Firestop Experts!

Best Regards,

Raymond Prescott V, Fire Protection Engineering Team

EJ Request Form,System Selector