Do penetrations through a roof need to be treated or protected with a firestop?

Posted by Johnpaul Goodeover 5 years ago
Do penetrations through a roof need to be treated or protected with a firestop?


firestop,roof penetrations

3 Replies
Posted by Raymondover 5 years ago
Answer Accepted


Hi Johnpaul. Thank you for checking out ASK Hilti! First, you should direct your attention to 2015 IBC code section 714.4. As you can see, only the “ceiling membrane of a roof/ceiling assembly” must be firestopped so that fire does not enter into the protected space of the roof/ceiling assembly.

Follow link to check out 2015 IBC for yourself!

-https://codes.iccsafe.org/public/document/IBC2015/chapter-7-fire-and-smoke-protection-features

Thank You for choosing Hilti as your Firestop Experts!

Best Regards,

Raymond Prescott V, Fire Protection Engineering Team

IBC,roof penetrations

Posted by Johnpaul Goodeover 5 years ago

So the answer is yes, there's a room membrane that may require firestopping?

If that is the case then what is the UL detail for it? I need a detail for electrical conduit penetrations.

conduit,room membrane

Posted by Raymondover 5 years ago

Great inquiry Johnpaul! We can create an engineering judgement to show you how to firestop a membrane penetration through a rated roof/ceiling assembly by submitting an EJ request form to usfirestopeng@hilti.com.

Follow link to request an engineering judgment:

https://www.hilti.com/content/hilti/W1/US/en/services/fasteners-firestop-strut/firestop-portfolio.html

Best Regards,

Raymond Prescott V, Fire Protection Engineering Team

EJ,EJ Request Form