Can you use ACI 318-14 with PROFIS Rebar?

Profis,Rebar,Profisrebar

1 Reply
Posted by Justin Bishopabout 8 years ago
Hilti Verified

Dear customer,

Well this is a good question. PROFIS Rebar calculations are based on the development and splice provisions given in ACI 318-11 Chapter 12. Per the ACI Transition Key for ACI 318-11 to ACI 318-14 and ACI 318.2-14, the development and splice provisions that are given in ACI 318-11 Chapter 12 and used by PROFIS Rebar to calculate tension and compression development/splice lengths have not changed in ACI 318-14.

PROFIS Rebar calculations for special moment frames and special structural walls are based on provisions given in ACI 318-11 Chapter 21. Per the ACI Transition Key for ACI 318-11 to ACI 318-14 and ACI 318.2-14, the provisions used in PROFIS Rebar to calculate development lengths for special moment frames and special structural walls have not changed in ACI 318-14.

Reference the ACI Transition Key for ACI 318-11 to ACI 318-14 and ACI 318.2-14 regarding a particular code section. Please feel free to reach out any time, if you need additional information.

Best Regards
Justin