Steel Element Failure

Posted by Robert Malouffalmost 5 years ago
Steel Element Failure

Can you ignore Steel Element Failure if a steel building designer shows they are adequate per AISC?

ANCHORS,Steel Element Failure

1 Reply
Posted by Adam Hastingsalmost 5 years ago
Hilti Verified

Hi Robert, just to clarify, do you mean the steel building designer is saying they designed the steel element (threaded rod/rebar/etc) being anchored into the concrete per AISC? What is the actual steel element being used in this case?

If your project is governed by ACI 318-14, then section 17.4 lays out the method for calculating design strength and comparing the tension failure modes which include steel element in tension, concrete breakout in tension, pullout/bond failure, and side-face blowout. Section 17.5 similarly lays out design strength calculations for the shear failure modes which include steel element in shear, concrete edge breakout, and pryout. The lowest capacity failure mode in tension and shear are considered your governing failure modes, and these are compared to your factored loads. If your factored loads are equal to or less than the governing design strengths in tension and shear, they will now have to pass the interaction check in section 17.6. All of this is assuming that you meet the requirements for edge distance, spacing, and concrete thickness in Section 17.7 and installation parameters in section 17.8.

The Engineer of Record (EOR) for the project could compare the capacity calculated for the steel element per AISC versus the design strengths calculated per ACI 318-14 Chapter 17. Ultimately it is up to the EOR to judge whether the calculation is adequate for the projects needs.

If you have further questions, please email our Technical Services team with specific details at deck@hilti.com.

Thanks,
Adam

failure,steel element,governing,failure mode

2 comments on this reply
Posted by Adam Hastingsalmost 5 years ago
Hi Robert, can you email specific details and, if possible, a PROFIS Engineering file to deck@hilti.com? Thanks, Adam

Posted by Robert Malouffalmost 5 years ago
Adam, This is for pre-engineered steel buildings. We receive the anchor bolt plans and reactions. The anchors are designed by the building designer. Their baseplates are already fabricated, in some cases, with the holes to receive their anchor bolts. Some of our designs per ACI318-14 determine steel failure. Our involvement is to design the foundation and anchor embedment. Using PROFIS we get a failure. These calculations must be submitted for permitting. This leaves us in a difficult position.