Penetration Firestopping System or Existing EJ

Posted by Bob Drakeabout 1 month ago
Penetration Firestopping System or Existing EJ

6" steel pipes, Qty 3, individual penetrations thru 2hr, 12" concrete wall. single side access. Annular space varies from 0" to maybe 1.5". I don't want to have wallboard in this area.

one-sided,steel pipe

1 Reply
Posted by Jessica Starksabout 1 month ago
Hilti Verified

Bob,

I have included WJ1088 and WJ1089, which is the most common one-sided solution for metallic penetrants through a concrete wall. If this system does not meet your needs, we can address your application through an Engineering Judgment, which will be a custom detail showing your exact application with the firestop components required to maintain the stated ratings.

Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP).This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)

Along with HCP, Hilti is excited to announce our new mobile app for all your firestop needs: Hilti FirestopSelector. Using the Firestop Selector app gives you easy access to the Hilti Fire Protection Design Team from the jobsite, on the road, or in the office to request a new EJ, an EJ Revision, or ask a Question anytime, anywhere.