Posted by vikry cendekiawanover 3 years ago
Maximum anchor size for injectable adhesive anchor

I designed an anchor group arrangement which require minimum 1 3/4 dia bolt. Does adhesive anchor still applicable for this particular size? what is the maximum bolt dia size for injection adhesive? (technical data sheet only show up to 1 1/4 in)

anchors for existing post tension concrete,epoxy adhesive,Post installed Anchor Bolt.

2 Replies
Posted by PARIS STANTONover 3 years ago
Hilti Verified

Hi Vikry,
 
Please refer to this answer from a previous question.

Regards,
Paris


1 comment on this reply
Posted by vikry cendekiawanover 3 years ago
Hi Paris, Well noted with thanks, As I checked the technical data, Its not shows the nominal bond capacity for 1 3/4" in. threaded rod, Could I use linear interpolation from the table to get the capacity for this size? Regards, Vikry

Posted by PARIS STANTONover 3 years ago

Vikry,
 
The referenced technical data is a result of testing. Therefore, the engineer on the project should use engineering judgment and on-site evaluation to determine suitability for applications outside the scope of the testing.

Regards,
Paris