Posted by Mohamed Maherover 6 years ago
Is hilti software design anchors based on Un reinforcement concert?

Hi all,

I have question Please I design base plate with moment around 580 Kn.m and 99 Kn shear .. this base plate should be fixed by hilti chemicals .. I found that i need at least 12 anchor and huge base plate size around 1200mmx 1200mm
is that possible. I have doubt Regarding these results.. with information that the concrete depth is 350 mm and fc=60 Mpa.. Kindly find the attached contain the hilti report. and advise if there is some thing not correct.

Thanks

Thanks Mr. Bryan for your replay i attached the hilti report, Kindly advise.

Best regards

Decreasing anchors Number,splitting failure,Concrete Cone failure taken in account that concrete is reinforced

2 Replies
Posted by Bryan Johnsonover 6 years ago
Hilti Verified

Mohamed,

Since this website is currently managed by personnel in the United States, we are not 100% proficient with the ETAG design standards, and the best option would be to discuss this application with a local Hilti representative. With that being said, it does appear in Section 1 that reinforcement, as well as longitudinal edge reinforcement, is being considered in the design. 

If you have any other questions, please feel free to contact us.

Regards, 

Bryan


Posted by Bryan Johnsonover 6 years ago
Hilti Verified

Mohamed,

It appears that your PROFIS Anchor Design Report did not attach to this conversation, so we are unable to review your file at this time.  With that being said though, from your question, it appears that you are asking whether or not PROFIS Anchor includes concrete reinforcement in its calculations.  If so, then under the "Base Material" tab, there is an option to modify the supplemental reinforcement (https://submittals.us.hilti.com/PROFISAnchorDesignGuide/#158/z) based on the user's inputs.

If you have additional questions, please feel free to contact us.

Regards,

Bryan


2 comments on this reply
Posted by Mohamed Maherover 6 years ago
Thanks Bryan that was helpful

Posted by Mohamed Maherover 6 years ago
Dear Bryan, Thanks for your replay , I added the hilti report at the questions kindly advise regarding this issue. Thanks again