Ask HiltiAskLearnArticles
Ask Hilti

Anchor to Metal Deck

Posted by TIAN LAN12 months ago
Anchor to Metal Deck

See attached for KWIK HUS-EZ anchor to Slab of Metal Deck. Why does the anchors shows more shear capacity when anchoring at upper flute compare to lower flute?

How is the capacity calculated?

Thanks

Slab on metal deck,anchoring bolt

1 Reply
Posted by Dani12 months ago
Hilti Verified

Hi Tianxiang,

The capacity comes from testing per the acceptance criteria, AC193, which is then published in ICC ESR-3027. Please reference Table 5 in the ESR linked for more information on the steel strength capacity. Additionally, the phi factors used in the calculations can be found in Table 3 of the same report. If you have additional questions please feel free to reach out to Hilti's engineers at 877-749-6337 or hnatechnicalservices@hilti.com.

Regards,
Dani

Steel Strength,COMD Calculations,AC193