Ask HiltiAskLearnArticles
Ask Hilti

How to Write a Basis-of-Design Specification for Anchors

Posted by Alexis Clark, P.E. (TX)over 4 years ago

Testing and Design Parameters that Affect Bond Strength of Adhesive Anchor Systems


4.1K

What should I specify when it comes to an adhesive anchor system?

ACI 318 17.8.2.1 acknowledges that the bond stress of adhesive anchors is dependent upon a variety of factors and requires structural engineers to consider and include those parameters in their design and specification. There are many factors, but three important and easily overlooked factors are:

  • Concrete temperature range at time of installation
  • Moisture condition of concrete at time of installation, and
  • Hole drilling and preparation.






Where can I find information about how these factors are addressed in my adhesive anchor design?

The International Code Council Evaluation Service (ICC-ES) writes acceptance criteria (AC) that reflects the provisions in ACI 355.4 Qualification of Post-Installed Adhesive Anchors in Concrete. ICC-ES likewise publishes an ICC-ES evaluation report (ESR) based on the acceptance criteria testing. These ICC-ES reports serve as a third-party evaluation with which engineers can compare engineered products. By meeting the Acceptance Criteria and having an ICC-ES report, manufacturers demonstrate compliance per reference model code. Adhesive anchors are tested to AC308 Acceptance Criteria for Post-Installed Adhesive Anchors in Concrete Elements

ICC-ES reports can include a vast amount of information:

  1. Check Section 2.0 Uses to ensure the product you’re designing with is intended for your application. Considerations may include, but not limited to, base material type, cracked or uncracked concrete, or development length provisions with rebar.
  2. Verify Section 3.0 Description includes the anchor element you intend to use; such as rebar, threaded rod or internally threaded inserts. Additionally, check the adhesive anchor system has been tested with dust-removal systems. While this may not be critical to you in the design phase, contractors maybe required to use OSHA 1926.1153 Table 1-compliant systems to reduce silica dust on jobsites.
  3. Read Section 5.0 Conditions of Use for applicable temperature ranges, installation orientations, and any other configuration requirements.
  4. Read Section 6.0 Evidence Submitted to verify the product you are evaluating has been tested in accordance with ICC-ES AC308.


How can these factors influence adhesive anchor performance?

Through reference and reliability testing per AC308, phi-factors are assigned to adhesive anchor products based on anchor diameter, continuous or periodic special inspection, hole-drilling methods, or moisture condition of the concrete. Higher phi-factors are associated with adhesives that perform more reliably and demonstrate less sensitivity to different conditions.




So why are these three parameters so important?

1) Moisture condition of concrete

When adhesives are installed into concrete holes and cure, they form a bond with the base material to transfer load from the anchor element. The presence of water can affect adhesion to the base material.

Per AC308, anchors can be tested to varying moisture conditions, including dry concrete, water-saturated concrete, water-filled concrete, and submerged concrete. Each product’s ICC-ES report includes phi-factors derived from testing in these conditions.

2) Temperature ranges

Adhesive anchors cure because of a reaction between a hardener and resin. That reaction can be accelerated or delayed depending on the temperature of the base material.

Temperature range impacts adhesive anchors in four ways:

  1. Adhesives are tested within a limited range of concrete temperatures at the time of installation. These temperatures are relevant to most installation conditions, but it’s important to verify that the concrete temperature at time at which your anchor is installed is within this range. Concrete temperature at the time of anchor installation can be influenced by geography, climate, and season.
  2. The time required for the adhesive to cure (cure time) will be longer at colder concrete temperatures and shorter at higher concrete temperatures. Reference the Manufacturer’s Printed Installation Instructions (MPII) for cure times.  
  3. The time permitted to install an adhesive anchor (working time or gel time) will also vary with concrete temperature. Reference the Manufacturer’s Printed Installation Instructions (MPII) for working times.
  4. Some products require conditioning to certain temperatures. For example, an ICC-ES report may state that the adhesive cartridge must be conditioned to 70 0F in base materials less than 70 0F in order to achieve performance consistent with the tested data.


3) Drilling and hole cleaning

When a hole is drilled into concrete, the hole surface may vary from rough to smooth depending on the drilling method. Additionally, the hole is likely to be filled with concrete dust and debris from the drilling process.

Hole cleaning steps typically consist of blowing out the hole with compressed air, brushing the hole with a steel wire brush, and blowing out of the hole again. This cleaning method can vary depending on the adhesive product. Reference the Manufacturer’s Printed Installation Instructions (MPII) for the cleaning method(s) specific to an adhesive product. Installer training on anchor installation per the MPII is also recommended.

Hilti’s SafeSet System was developed to simplify the hole cleaning steps by using either (a) a hollow-drill bit and vacuum system that removes dust and debris during the drilling process or (b) a proprietary anchor element, such as a Hilti HIT-Z rod, requires no hole cleaning to transfer load. Since OSHA’s increased silica dust regulations in 2016, other anchor manufacturers have developed similar technology for the purpose of silica dust removal and compliance with OSHA 1926.1153 Table 1.

 
How do I fit all of this important information into my anchor specification?

1) Include “Basis of Design” parameters in your General Notes.



2) Call out the specific product, anchor diameter and embedment depth, and hole drilling and cleaning method directly in your details.


3 comments on this article
Posted by PARIS STANTONabout 4 years ago
https://submittals.us.hilti.com/PTGVol2/#1/z

Posted by PARIS STANTONabout 4 years ago
Hi Efrain, The minimum spacing between anchors will depend on the type and size of anchor. Here is the link to the Product Technical Guide for Anchor Fastening. The minimum spacing can be found in the section for each specific anchor. Regards, Paris

Posted by efrain arvizuabout 4 years ago
Is there a minimum space distance between the two and the four anchors? Most HSS posts tend to be no more that 3" on the front face and 5" on the side face, to hide within curtain wall system or other architectural open system.